The Cove Business Standards Discussion Forums More Free Files Forum Discussion Thread Post Attachments Listing Cove Discussion Forums Main Page
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
UL - Underwriters Laboratories - Health Sciences
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7
Go Back   The Elsmar Cove Business Systems and Standards Discussion Forums > >
Forum Username

Elsmar Cove Forum Visitor Notice(s)

Wooden Line

ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7


Elsmar XML RSS Feed
Elsmar Cove Forum RSS Feed

Monitor the Elsmar Forum
Sponsor Links




Courtesy Quick Links


Links Elsmar Cove visitors will find useful in the quest for knowledge and support:

Jennifer Kirley's
Conway Business Services


Howard's
International Quality Services


Marcelo Antunes'
SQR Consulting, and
Medical Devices Expert Forum


Bob Doering
Bob Doering's Blogs and,
Correct SPC - Precision Machining


Ajit Basrur
Claritas Consulting, LLC



International Standards Bodies - World Wide Standards Bodies

ASQ - American Society for Quality

International Organization for Standardization - ISO Standards and Information

NIST's Engineering Statistics Handbook

IRCA - International Register of Certified Auditors

SAE - Society of Automotive Engineers

Quality Digest

IEST - Institute of Environmental Sciences and Technology


Some Related Topic Tags
cleanroom classification, cleanrooms, iso 14644 - cleanrooms and controlled environments, particle counts
Reply
 
Thread Tools Search this Thread Rate Thread Content Display Modes
  Post Number #1  
Old 1st November 2011, 08:03 AM
SGquality

 
 
Total Posts: 257
Thank You! ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Class 7

I have a question on the ISO Class 7 clean rooms.

When do perform particle counts of the clean rooms, it complies as per the requirements of ISO Class 7 (10,000) consistently as defined per ISO 14644 standard.

Is this requirement okay to label the clean room as per ISO Class 7 ? My question is specifically because when we built the clean room, it was to comply per ISO Class 8 clean rooms (100,000) but since the particle counts are met per Class 7 areas, our Management label it as ISO Class 7 area.

Is this acceptable ? Or is there anything that needs to be carried out seperately per ISO Class 7 ?

Thanks in advance


Sponsored Links
  Post Number #2  
Old 2nd November 2011, 01:39 AM
Stijloor's Avatar
Stijloor

 
 
Total Posts: 15,219
Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Quote:
In Reply to Parent Post by SGquality View Post

I have a question on the ISO Class 7 clean rooms.

When do perform particle counts of the clean rooms, it complies as per the requirements of ISO Class 7 (10,000) consistently as defined per ISO 14644 standard.

Is this requirement okay to label the clean room as per ISO Class 7 ? My question is specifically because when we built the clean room, it was to comply per ISO Class 8 clean rooms (100,000) but since the particle counts are met per Class 7 areas, our Management label it as ISO Class 7 area.

Is this acceptable ? Or is there anything that needs to be carried out separately per ISO Class 7 ?

Thanks in advance

Can someone help?

Thank you very much!!

Stijloor.
Sponsored Links

  Post Number #3  
Old 2nd November 2011, 03:53 AM
harry

 
 
Total Posts: 6,290
Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Quote:
In Reply to Parent Post by SGquality View Post

...................when we built the clean room, it was to comply per ISO Class 8 clean rooms (100,000) but since the particle counts are met per Class 7 areas, our Management label it as ISO Class 7 area. .........................
Amazing! Unless somebody replaced the filters. Otherwise, my first suspicion will be on how the particles counts were measured. Did you get an independent lab to verify it?
  Post Number #4  
Old 2nd November 2011, 04:12 AM
somashekar's Avatar
somashekar

 
 
Total Posts: 5,253
Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Quote:
In Reply to Parent Post by SGquality View Post

I have a question on the ISO Class 7 clean rooms.

When do perform particle counts of the clean rooms, it complies as per the requirements of ISO Class 7 (10,000) consistently as defined per ISO 14644 standard.

Is this requirement okay to label the clean room as per ISO Class 7 ? My question is specifically because when we built the clean room, it was to comply per ISO Class 8 clean rooms (100,000) but since the particle counts are met per Class 7 areas, our Management label it as ISO Class 7 area.

Is this acceptable ? Or is there anything that needs to be carried out seperately per ISO Class 7 ?

Thanks in advance

The other way could happen, but from what you say, I would take an other validation run with workload situation to reassess if indeed it meets the class 7 consistently.
To maintain class 7 the man and material control could be a lot different, and you must consider this.
If I were you, I would apply caution and wait for repeated validation over time.
  Post Number #5  
Old 2nd November 2011, 04:55 AM
Kwesifaiola

 
 
Total Posts: 4
Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Hello
Thanks for provide me information about ISO standards class because this will help me.
Thanks
Regards
Kwesifaiola
  Post Number #6  
Old 3rd November 2011, 12:52 AM
SGquality

 
 
Total Posts: 257
Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Quote:
In Reply to Parent Post by harry View Post

Amazing! Unless somebody replaced the filters. Otherwise, my first suspicion will be on how the particles counts were measured. Did you get an independent lab to verify it?
Yes harry - all the particulates are measured by an external laboratory and there is no doubt on measurements. In fact the limits for particulate counts are so huge that most ISO Class 8 clean rooms areas would be acceptable at the higher classification too as the particle counts are low.

Quote:
In Reply to Parent Post by somashekar View Post

The other way could happen, but from what you say, I would take an other validation run with workload situation to reassess if indeed it meets the class 7 consistently.
To maintain class 7 the man and material control could be a lot different, and you must consider this.
If I were you, I would apply caution and wait for repeated validation over time.
Thanks somashekhar. That was my precise question. What would be different in these 2 areas ?
  Post Number #7  
Old 5th November 2011, 01:19 AM
SGquality

 
 
Total Posts: 257
Question Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Pls help

  Post Number #8  
Old 5th November 2011, 02:41 AM
somashekar's Avatar
somashekar

 
 
Total Posts: 5,253
Re: ISO Class 7 Clean Rooms - built as Class 8 but complies with requirements of Clas

Quote:
In Reply to Parent Post by SGquality View Post

Pls help

Not knowing your product that you handle in the clean room, it is not too easy to suggest. However the selction of the clean room class and the processes performed thereafter as against requirement is a matter of risk assessment and supported by valid product testing.
Calling out your clean room as Class 7 and yourself is far less important than claiming meeting or exceeding class 8 and supporting the same with periodic validation and product test reports meeting to requirements.
Reply

Lower Navigation Bar
Go Back   The Elsmar Cove Business Systems and Standards Discussion Forums > >

Bookmarks



Visitors Currently Viewing this Thread: 1 (0 Registered Visitors (Members) and 1 Unregistered Guest Visitors)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Forum Search
Display Modes Rate Thread Content
Rate Thread Content:

Forum Posting Settings
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Emoticons are On
[IMG] code is On
HTML code is Off


Similar Discussion Threads
Discussion Thread Title Thread Starter Forum Replies Last Post or Poll Vote
Clean Room Cost per sq foot is to have a class 100,000 clean room built erniel Manufacturing and Related Processes 3 24th March 2015 06:26 PM
Electrical Class (Class I, II & III) vs. Medical Device CE marking Class I, II & III LuckyK ISO 13485:2016 - Medical Device Quality Management Systems 3 6th January 2015 12:43 PM
Do I need to test "as built" for an expanded ISO Class 8 Clean Room ? dcvanderbush Other Medical Device Related Standards 2 2nd April 2014 03:01 PM
The requirements of an ISO 14644 Class 8 Clean Room SK Vision Manufacturing and Related Processes 1 17th July 2009 09:17 AM
Percentage of Class I Medical Devices in market - viz Class I, Class II and Class III Ajit Basrur ISO 13485:2016 - Medical Device Quality Management Systems 8 25th February 2008 04:44 AM



The time now is 12:43 AM. All times are GMT -4.
Your time zone can be changed in your UserCP --> Options.


 
 
 


NOTE: This forum uses "Cookies"