Q
A have a field test instrument (fluke meter) that I use on a Class 5 furnace to perform the SATs. Section 3.2.5.3 says we have to check sensitivity and points to Table 3 note 4. That note in Table 3 only applies to control, monitoring, or recording instruments.
Can someone help clarify if I need to check sensitivity on a field test instrument during calibration? If so, do I default to the Class of furnace I am using it on (e.g. class 5 requirements)?