I am currently working with an electrical engineering consultancy practice.95% of their work is the production of technical reports. however 5% involved design.
the practice operates in the renewable energy sector and advices companies wishing to build wind farms and power stations how the can connect to the national grid.
The elements of the design that they do may involve such things as electrical design diagrams and specification for sizing of plant and cabling to the national grid.
My question is as follows: is validation of design a justifiable exclusion in that the scope of work provided by the practice extends only to the design itself. they do not get involved in the commissioning of the plant.
my wording of the justification for the exclusion is as follows:
"Since the product is the design itself, the customer in effect validates the design and provides feedback to the designer. Performance at the extremities of the design range may never be validated, particularly if they are based on rare occurrence or may not be validated for some time e.g. where there is a design life of many years. Thus the company views this clause to be justifiable exclusion."
Your views on our intrepretation would be greatly appreciated.:confused:
BradM
Re: Design Validation - Justifiable Exclusion for an Electrical Engineering Consultan
Hello there!:bigwave:
The practice operates in the renewable energy sector and advices companies wishing to build wind farms and power stations how the can connect to the national grid.
While it's true they are not designing anything, per se. They have a process they use to advise clients of how they should connect to the grid. This process that they use should be validated, should it not?
tonyjj
Hi Brad,
They are doing design the 5% I stated they can verify the design via calculations but cannot validate it as they are only providing the design. it is my understanding that as they are not involved in the comissioning they cannot validate the design. also all design have safety factors built into them so they may be impossible to every validate the design unless for some reason the power output exceeds the design limits correct?
Brad i am not talking about process validation I'm talking about design validation.
Big Jim
I believe they can validate, at least as much as possible. And they likely do.
Remember that validation is determining if it is suitable for its intended use.
Also remember that the standard requires validation for the specified application "where known".
"Design and development validation shall be performed in accordance with planned arrangements to ensure that the resulting product is capable of meeting the requirements for the specified application or intended use, where known."
It is even possible that what you are doing as verification may either actually be validation, or at least might be doing some of both.
I don't think I would try to claim an exclusion for this also because of the qualifications for exclusion.
"Where exclusions are made, claims of conformity to this international standard are not acceptable unless these exclusions are limited to requirements within clause 7, and such exclusions do not affect the organization's ability, or responsibility, to provide product that meets customer and applicable statutory requirements."
I suspect that your ability or responsibility to provide viable product would be compromised.
BradM
Hi Brad,
They are doing design the 5% I stated they can verify the design via calculations but cannot validate it as they are only providing the design. it is my understanding that as they are not involved in the commissioning they cannot validate the design. also all design have safety factors built into them so they may be impossible to every validate the design unless for some reason the power output exceeds the design limits correct?
:agree1:
Good explanation. I still might suggest the design efforts can be validated. If you were designing drapes for a window:D, I would think it's no big deal. But for that line of work, I think you would want to assure the steps in designing the hookup to the grid are safe, and follow industry guidelines/ practices.
It may be as simple as assuring the calculations used produce the intended result, the calculations made are repeatable and reliable, and all various combinations in the the calculations are considered.
Tony... this is the weekend, and things are a bit slow. Hopefully next week some other folks can offer their opinions.
Chennaiite
Never-say-die
Hi Brad,
Tony, just a question. If Design Validation results are not OK, who is responsible for re-Design ? I am sure it is going to be you, as a Design responsible Organization. It is really immaterial whether or not Validation is carried out by you, responsibility still remains with you.
harry
The act of a Professional Electrical Engineer inking his 'P. Eng Stamp' and signature on the final design drawings is 'validation'. It means that he had checked the design (including the necessary calculations) and from his professional experience and knowledge, he certifies that the design is workable and conforms with the necessary regulatory requirements. Such designs or project are still subject to adjustments and amendments (re-designs, further details, etc) at site to cope with unknowns and uncertainties in most major projects.
Also bear in mind that Consultancy is basically a service and 'design' is also applicable for the service part.
harry
..............................they can verify the design via calculations but cannot validate it as they are only providing the design. it is my understanding that as they are not involved in the comissioning they cannot validate the design. ...................
If you are not familiar with practices in 'projects' type of environment, this may help you to an extent: Auditing the Design and Development Process. Read the part on Auditing Design and Development Validation (section 8, bottom part).
tonyjj
Hello Everyone
The feedback back by everyone has been very worth while and i really appreciate your views.:):agree1::applause:
Are we saying then that, in this case the design review verification and validation activities are the same thing. this is acknowegded as being ok in one of the foot notes within 7.3.
So then would anyone have an eample of a design review checklist to get me started?
Finally, to Marc,as always the links to other threads of a similar nature has been invaluable and comments are concurrent with replys on this trend.
:thanx:
Colin
Are we saying then that, in this case the design review verification and validation activities are the same thing. this is acknowledged as being ok in one of the foot notes within 7.3
Tony, as you say, the note at the end of 7.3.1 states 'design and development review, verification and validation have distinct purposes. They can be conducted and recorded separately or in any combination, as suitable for the product and the organisation'.
So if you want to combine them to suit your situation then you can.
However, it is my understanding that validation should be done on the finished product wherever possible. So could you get evidence of the finished installation tests sent back to you in order to 'close the loop'?
M API 4F/7K/8C Design Package Validation Oil and Gas Industry Standards and Regulations 2
D Test summary report example for design validation wanted - ISO 13485 ISO 13485:2016 - Medical Device Quality Management Systems 1
P Design verification driven by new equipment. How is this different than process validation? 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 1
K Old medical devices -> 7.3.7. Design and development validation ISO 13485:2016 - Medical Device Quality Management Systems 1
N Design Verification & Process Validation - Statistical sample sizes Design and Development of Products and Processes 2
C Design Transfer Review - Before or after PQ validation? 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 5
V Which batches should or could be considered for design validation and design verification? 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 0
T Sample Size for Design Validation Design and Development of Products and Processes 4
J Is Design Validation required for fixtures or test systems used to manufacture a product? AS9100, IAQG, NADCAP and Aerospace related Standards and Requirements 4
P Performance evaluation (IVDD Annex VIII) & Design and Development Validation Studies EU Medical Device Regulations 1
S Source of QMS templates including templates for design verification/design validation Document Control Systems, Procedures, Forms and Templates 2
L Why is initial production units, lots, or batches, or their equivalents required for Design Validation? US Food and Drug Administration (FDA) 3
S Is Human Factor Testing required as part of Design Control Validation? 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 3
W Design and Process Validation - Different? ISO 13485:2016 - Medical Device Quality Management Systems 6
C Partial Design Validation and changes to a critical supplier 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 4
N Design Validation Conventions for Design History Files 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 5
S CE Mark Approval Design Verification and Validation Questions CE Marking (Conformité Européene) / CB Scheme 8
J Design Control - Can Validation be based on a limited/first Production Run ISO 9000, ISO 9001, and ISO 9004 Quality Management Systems Standards 3
C MSA for Non Manufacturing - Design Validation, Characterization and Qualification Lab Gage R&R (GR&R) and MSA (Measurement Systems Analysis) 3
N How to perfom Design Validation for Road Designs Design and Development of Products and Processes 14
J Where does process validation fit within design & development? Design and Development of Products and Processes 7
T ISO 9001 - Design Validation Record exemption ISO 9000, ISO 9001, and ISO 9004 Quality Management Systems Standards 15
A Products for Design Validation - FDA Requirements US Food and Drug Administration (FDA) 3
S Can anyone provide an example of Design Validation Protocol and Report? 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 2
H Is design verification and validation required for samples accompanying the quotes ? ISO 9000, ISO 9001, and ISO 9004 Quality Management Systems Standards 5
S Verification and Validation of Post Market Design Change Design and Development of Products and Processes 2
A Determination of Production Equivalence for Design Validation 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 1
Chennaiite How to Measure Effectiveness of the Design Validation Process? Design and Development of Products and Processes 7
A Finishing Design Validation per 21 CFR Part 820 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 6
K Medical Device Design Validation vs Clinical Evaluation ISO 13485:2016 - Medical Device Quality Management Systems 5
M Design and Development Validation at the Customer's Location Document Control Systems, Procedures, Forms and Templates 5
P How to separate Product Design Review, Verification, and Validation Activities ISO 9000, ISO 9001, and ISO 9004 Quality Management Systems Standards 26
M Design and Development Outputs Approval, Verification and Validation IATF 16949 - Automotive Quality Systems Standard 4
G Legacy Product - Do we need follow QSR 820? Design Verification and Validation 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 12
A How to do Medical Device Design Validation 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 15
S Design and Development - Review vs. Verification vs. Validation Design and Development of Products and Processes 15
G Sample Size for Design Verification and Validation 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 6
L Design Validation Process Owner - Who should be the process owner of validation? ISO 9000, ISO 9001, and ISO 9004 Quality Management Systems Standards 5
B Is Ship Test considered Design Verification or Design Validation? 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 2
D Design Input/Output and Design V&V (Verification and Validation) Interpretations 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 14
D Medical Device Design Verification and Validation Differences 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 16
Chennaiite Prototype - Design Verification or Validation? APQP and PPAP 12
B Validation of DoE (Design of Experiements) Model - Minitab 15 Using Minitab Software 3
I Cumulative Confidence Levels - Design Verification and Validation Sampling Inspection, Prints (Drawings), Testing, Sampling and Related Topics 12
B Sample Sizes for In-Vivo Design Validation Testing Other Medical Device and Orthopedic Related Topics 1
S Medical Device Design Verification and Validation - info Other Medical Device and Orthopedic Related Topics 1
S Design Validation Work Instruction - Help 21 CFR Part 820 - US FDA Quality System Regulations (QSR) 3
D Special 510k - Data Results of the Design Verification and Validation Other US Medical Device Regulations 3
E Determining Sample Size for Design Verification and Design Validation Other Medical Device and Orthopedic Related Topics 20